Hallo PVSol Team,

I was wondering how PVSol calculates the rating of circuit breakers needed after the inverter and after the bidirectional meter for a system. z.B. the following system uses Solaredge SE7K 3 phase inverter with max output current per phase of 11,5 Amp. PVSol suggested a 16A breaker. Could you please explain how this suggestion was made?

Thanks.

image.thumb.png.2c650a049b886c72a41516d555f4489a.png

  • Like 1
Posted

Dear Vishnu,

the current rating for the circuit breakers is determined as follows:

  • Determine the maximum AC current of the connected inverters (taking into account the maximum AC output power, the grid voltage and the number of phases)
  • Apply safety factor of 1.1
  • Choose the smallest current rating that is bigger than this current from the list:
    • 6, 10, 13, 16, 20, 25, 32, 40, 50, 63, 80, 100, 125 A
  • The characteristic is always B, except for inverters with transformator (K) oder with ENS (C)

Hope that helps, kind regards,

Martin

  • Thanks 1
Posted

Hey Martin,

I remember that NEC requries rating the breakers at 125% the full load current. Please correct me if I am wrong. 

Is it different in case of PV systems when it comes to breakers for inverters?

Danke!!!

-Vishnu

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...