January 21, 20206 yr comment_3321 Hallo PVSol Team, I was wondering how PVSol calculates the rating of circuit breakers needed after the inverter and after the bidirectional meter for a system. z.B. the following system uses Solaredge SE7K 3 phase inverter with max output current per phase of 11,5 Amp. PVSol suggested a 16A breaker. Could you please explain how this suggestion was made? Thanks. Report
January 22, 20206 yr comment_3326 Dear Vishnu, the current rating for the circuit breakers is determined as follows: Determine the maximum AC current of the connected inverters (taking into account the maximum AC output power, the grid voltage and the number of phases) Apply safety factor of 1.1 Choose the smallest current rating that is bigger than this current from the list: 6, 10, 13, 16, 20, 25, 32, 40, 50, 63, 80, 100, 125 A The characteristic is always B, except for inverters with transformator (K) oder with ENS (C) Hope that helps, kind regards, Martin Report
January 30, 20206 yr Author comment_3367 Hey Martin, I remember that NEC requries rating the breakers at 125% the full load current. Please correct me if I am wrong. Is it different in case of PV systems when it comes to breakers for inverters? Danke!!! -Vishnu Report