Vishnu Posted January 21, 2020 Report Posted January 21, 2020 Hallo PVSol Team, I was wondering how PVSol calculates the rating of circuit breakers needed after the inverter and after the bidirectional meter for a system. z.B. the following system uses Solaredge SE7K 3 phase inverter with max output current per phase of 11,5 Amp. PVSol suggested a 16A breaker. Could you please explain how this suggestion was made? Thanks. 1 Quote
developer_mh Posted January 22, 2020 Report Posted January 22, 2020 Dear Vishnu, the current rating for the circuit breakers is determined as follows: Determine the maximum AC current of the connected inverters (taking into account the maximum AC output power, the grid voltage and the number of phases) Apply safety factor of 1.1 Choose the smallest current rating that is bigger than this current from the list: 6, 10, 13, 16, 20, 25, 32, 40, 50, 63, 80, 100, 125 A The characteristic is always B, except for inverters with transformator (K) oder with ENS (C) Hope that helps, kind regards, Martin 1 Quote
Vishnu Posted January 30, 2020 Author Report Posted January 30, 2020 Hey Martin, I remember that NEC requries rating the breakers at 125% the full load current. Please correct me if I am wrong. Is it different in case of PV systems when it comes to breakers for inverters? Danke!!! -Vishnu Quote