Good morning,

 

I am having problems connecting modules. I'm designing a 1.42 MWp photovoltaic plant, I am in the connection stage, and I have noticed the following issues:

 

1.- As you can see in the first image, I have used some surfaces to use panels from other areas in order to fully utilise the inverter's MPPT. Perhaps because it is a large system, the wiring plan options where I can use groupings, cable glands, etc. no longer appear, as shown in the second image. Why is this? I would like to place these items and have a breakdown of how much cable I am estimated to use, as shown in the third image

 

2.- The next new feature concerns the connection of photovoltaic modules. As you can see in the fourth and fifth image, I have used solar panels on both sides of a building, leaving the connection provided by the programme by default when I have two sides. However, if I try to modify that connection and go to the wiring plan, the programme completely distorts the connection and pretends that it is not using the panels on the other side of the building, as you can see in the sixth and seventh image. So I have made a connection that is not as viable as in the eighth image because of the error that appears, since if I modify the module connections when I use multiple areas, the connection is distorted; even those panels appear without a connection.

 

I would appreciate any support that would help me resolve these issues.

 

I look forward to your comments. Thank you.

Figure1.png

Figure2a.png

Figure2b.png

Figure3a.png

Figure3b.png

Figure4a.png

Figure4b.png

Figure5.png

Posted

Dear J. Esteban,

Thank you for your inquiry.

Unfortunately, the cable plan is not available for elevated systems or polystring configurations. Alternatively, you can use the string diagram. However, cable lengths and diameters cannot be calculated automatically here; you must define them under Cables after exiting the 3D visualisation.

If you have already created a cable plan and subsequently make changes to the configuration, the cable/string diagram is not always updated. You must then delete the cable plan (press the ‘Delete all cables’ button), switch back to the Module configuration page and then back to the Cable plan page. Everything is then updated and the cables run in accordance with the configuration.

For large systems with complex string distribution we recommend that you manually define module areas for each string or MPPT (with the specified string or MPPT number) using the "Define module areas for configuration" function, as also explained here. First delete the existing inverter configuration. In the "Module Configuration" tab, select all modules for one string or MPPT by holding down the CTRL key and select "Add to "Define module areas" dialogue" with the right mouse button. Then click "Define module areas for Configuration". Rename the module areas (right-click --> Rename). Repeat this for all module areas belonging to the same inverter. Then click "configure" and configure inverter 1 (configure all selected Module Areas together and use Polystring Configuration). Repeat these steps for all inverters. The subsystems will then have a fixed inverter assignment. Direction, starting point and course of a string can be defined in the bottom left corner. The module sequence within a string must be changed manually if required.

You can also send your project file (*.pvprj) to hotline@valentin-software.com so that we can take a closer look at it.

Posted
1 hour ago, hotline_oh said:

Estimado J. Esteban,

Gracias por su consulta.

Desafortunadamente, el plan de cable no está disponible para sistemas elevados o configuraciones de polistrings. Alternativamente, puede usar el diagrama de cadenas. Sin embargo, las longitudes y diámetros de los cables no se pueden calcular automáticamente aquí; debe definirlos en Cables después de salir de la visualización 3D.

Si ya ha creado un plan de cables y posteriormente realiza cambios en la configuración, el diagrama de cables/cuerdas no siempre se actualiza. A continuación, debe eliminar el plan de cables (presione el botón 'Eliminar todos los cables'), volver a la página de configuración del módulo y luego volver a la página del plan de cables. A continuación, todo se actualiza y los cables se ejecutan de acuerdo con la configuración.

Para sistemas grandes con distribución de cadenas compleja, le recomendamos que defina manualmente las áreas de módulo para cada cadena o MPPT (con la cadena o el número MPPT especificado) utilizando la función "Definir áreas de módulo para configuración", como también se explica aquí. Primero elimine la configuración del inversor existente. En la pestaña "Configuración del módulo", seleccione todos los módulos para una cadena o MPPT manteniendo presionada la tecla CTRL y seleccione "Agregar al cuadro de diálogo "Definir áreas de módulos" con el botón derecho del mouse. A continuación, haga clic en "Definir áreas de módulos para la configuración". Cambie el nombre de las áreas del módulo (haga clic con el botón derecho en --> Cambiar nombre). Repita esto para todas las áreas del módulo que pertenecen al mismo inversor. Luego haga clic en "configurar" y configure el inversor 1 (configure todas las áreas de módulo seleccionadas juntas y use la configuración de polistrings). Repita estos pasos para todos los inversores. Los subsistemas tendrán entonces una asignación de inversor fija. La dirección, el punto de partida y el curso de una cadena se pueden definir en la esquina inferior izquierda. La secuencia del módulo dentro de una cadena debe cambiarse manualmente si es necesario.

También puede enviar su archivo de proyecto (*.pvprj) a hotline@valentin-software.com para que podamos verlo más de cerca.

Good morning,

 

Now that the first point has been clarified, just yesterday I discovered that “trick” for fixing connections in multiple areas.

 

Regarding the second point, it's great that connections can be made that way! I'll try it again, making the connection that way and changing the names of the surfaces. I think it will be easier to modify connections by system so that there is not just one and to prevent all connections from being activated at the same time.

 

I will share the project with you by email. I have not yet completed the connections as I am still defining them to minimise losses due to voltage drops.

 

Thank you very much for your help!

Posted

Dear J. Esteban,

Thank you for sharing the project file.

We strongly recommend defining a separate sub-system for each inverter. This way, if you need to remove or add a single PV module at the end, you don't have to redo the entire wiring, just the wiring for the inverter in question.

We would like to show you how to  manually define module areas for each string or MPPT (with the specified string or MPPT number) using the "Define module areas for configuration" function. First delete the existing inverter configuration. In the "Module Configuration" tab, select all modules for one string or MPPT by holding down the CTRL key and select "Add to "Define module areas" dialogue" with the right mouse button. Then click "Define module areas for Configuration".

image.png

Rename the module areas (right-click --> Rename). 

image.png

Repeat this for all module areas belonging to the same inverter. Use the drop-down menu to switch to the second building.

image.png

Then click "configure" and configure inverter 1 (configure all selected Module Areas together).

image.png

image.png

Repeat these steps for all inverters. The subsystems will then have a fixed inverter assignment. Direction, starting point and course of a string can be defined in the bottom left corner. The module sequence within a string must be changed manually if required.

image.png

  • 2 weeks later...
Posted
On 9/18/2025 at 3:24 AM, hotline_oh said:

Dear J. Esteban,

Thank you for sharing the project file.

We strongly recommend defining a separate sub-system for each inverter. This way, if you need to remove or add a single PV module at the end, you don't have to redo the entire wiring, just the wiring for the inverter in question.

We would like to show you how to  manually define module areas for each string or MPPT (with the specified string or MPPT number) using the "Define module areas for configuration" function. First delete the existing inverter configuration. In the "Module Configuration" tab, select all modules for one string or MPPT by holding down the CTRL key and select "Add to "Define module areas" dialogue" with the right mouse button. Then click "Define module areas for Configuration".

image.png

Rename the module areas (right-click --> Rename). 

image.png

Repeat this for all module areas belonging to the same inverter. Use the drop-down menu to switch to the second building.

image.png

Then click "configure" and configure inverter 1 (configure all selected Module Areas together).

image.png

image.png

Repeat these steps for all inverters. The subsystems will then have a fixed inverter assignment. Direction, starting point and course of a string can be defined in the bottom left corner. The module sequence within a string must be changed manually if required.

image.png

 

Dear Sirs,

Thank you for your recommendation. I've followed those steps and the issue of having separate systems has improved.

I have another question. Is there a way for the programme to determine the amount of DC cabling from the strings to the inverter? Is it possible to establish a reference point for where the inverters are located and then indicate which MPPTs they would be connected to?

I would need information on the estimated amount of DC cable I'll use in order to quantify the total length required.

I look forward to your prompt response.

 

Posted

Dear J. Esteban,

Thank you for your inquiry.

Automatic cable dimensioning is only available for roof-parallel systems, not for elevated systems or systems with polystring connection.

Cable nodes and cable grommets can be added to the cable plan using drag & drop.

image.png

It is not possible to establish a reference point for where the inverters are located. The length of the DC cables is calculated from the PV modules to the cable grommets. The cable lengths are displayed in the cable list.

image.png

Press the F1 key to access the help page for cable dimensioning.

image.png

  • 1 month later...
Posted (edited)

Good afternoon,

Would it be possible for me to send you the final project design so that you could perhaps provide some guidance on how to prepare the cabling layout, please?

At the moment, I’m considering carrying out the cabling separately for each roof inclination — that is, one layout per roof face. This would of course require selecting different types of inverters to enable the automatic cabling configuration, according to the capacity of each roof slope. From there, I could develop a more detailed cabling plan.

I mention this because I will soon have the solar cable reels in stock, and I need to quantify the amount required specifically for this project.

Thank you in advance for your assistance. I look forward to your comments.

Kind regards

Edited by J. Esteban
Posted
5 hours ago, hotline_oh said:

Dear J. Esteban,

Thank you for your inquiry.

Please send you project file (*.pvprj) to hotline@valentin-software.com, so we can take a look.

Good morning,

I will be sending the simulations by email shortly for your review; I’ll provide further details in the message.

I appreciate your assistance in advance.

Kind regards.

  • 4 weeks later...
Posted
On 11/13/2025 at 3:20 AM, hotline_oh said:

Dear J. Esteban,

Thank you for your inquiry.

Please send you project file (*.pvprj) to hotline@valentin-software.com, so we can take a look.

Good morning,

After reading your suggestions that the cabling can only be routed over surfaces, I wanted to check something with you. Does this mean I also wouldn’t be able to obtain the estimated solar cable length if I run a ground-mounted layout with module supports?

I’d appreciate any guidance you can offer. I’ve attached an image showing how I currently have the design set up.

Kind regards.

Screenshot_Captura de pantalla01.jpg

Posted

Dear J. Esteban,

Thank you for your inquiry.

Automatic cable dimensioning is only available for roof-parallel systems, not for elevated systems or systems with polystring connection.

Since your system is very uniform and the module tables are mounted very flat, you would have the option of treating it like a rooftop system, i.e., creating a pitched roof with minimal height and the same number of modules with roof-parallel mounting, in order to be able to carry out the automatic cable dimensioning.

  • Thanks 1

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...