Does anyone know if PVSOL is able to model DC couple battery energy storage systems? In the UK DNOs regard AC coupled BESS inverters as generators and DC couple BESS can also make use of DC power shaved off at peak generation by undersized AC inverters

Posted

Dear Solarific,

yes, in PV*SOL you can also use DC coupled battery systems. There are three kinds of coupling:

  • AC coupling (coupling takes place on the AC side, after the PV inverter)
  • DC intermediate circuit coupling (coupling takes place inside the PV inverter, in the DC intermediate circuit, i.e. before the DC/AC stage)
  • DC generator coupling (coupling takes places on the DC string, before the PV inverter)

See more information and grafics here:

https://help.valentin-software.com/pvsol/en/calculation/battery-systems/#type-of-coupling

Hope that helps, kind regards,

Martin

  • 2 years later...
Posted
On 11/16/2021 at 11:55 PM, developer_mh said:

Dear Solarific,

yes, in PV*SOL you can also use DC coupled battery systems. There are three kinds of coupling:

  • AC coupling (coupling takes place on the AC side, after the PV inverter)
  • DC intermediate circuit coupling (coupling takes place inside the PV inverter, in the DC intermediate circuit, i.e. before the DC/AC stage)
  • DC generator coupling (coupling takes places on the DC string, before the PV inverter)

See more information and grafics here:

https://help.valentin-software.com/pvsol/en/calculation/battery-systems/#type-of-coupling

Hope that helps, kind regards,

Martin

Hi friend, How can i change coupling system type ?

Posted

Hi Black,

thanks for your question.

The coupling type can only be changed for self-created or copied entries:

image.png

You can create a new entry or copy an existing entry with the action buttons on the top of the table or by right click on the table:

image.png

Kind regards

Mikio

  • Like 1
  • 1 year later...
Posted

Is there a way to get this to operate with a certain sized inverter? In the case of the UK say the DNO has given a constraint of 100kW export and so you want a 300kW PV system with a DC/DC battery of say 500kW that can only export a maximum of 100kW after the battery DC/AC.

Posted

Dear m.hall747,

Thank you for your inquiry.

The desired setting (maximum feed-in power of 100 kW at the inverter or at the feed-in point) can be configured under "Options" --> "Project Options" --> "AC Mains" (regardless of the inverter used).

image.png

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...