Good Day, I want to make sure if my calculations are correct. I added a Dyness PowerBlock Max 16kWh battery to the database. Please just check if my Discharge Cycles are correct below:

image.png.4523515ad50e7743dc131051103eb60d.png

image.thumb.png.126a08f19ddb1fdeca700453a98e4acf.png

image.png

Posted

When I try to change the value at 60% DOD to 10000 and do the Calculate cycles then that value just returns back to the values that it was. Nothing changes.

Also please give me the formula to determine a batteries DOD at 60% from the datasheet.

image.thumb.png.8007582194a53ec77c7fe40afc1154bc.png

Posted

Dear Mark,

We apologise: for lithium iron phosphate batteries, the reference value used to calculate discharge cycles is not a DoD of 60% (as with lead-acid batteries), but a DoD of 40%.

You can simply enter these four values manually:

image.png

We are still awaiting feedback from our development department regarding the formula.