Ho is this possible below if you have 9 x Jink0 590Watt BDV panels installed. The VOC of these panels is 52.9Vdc and multiplied by 9 gives you 476.1Vdc, and not 519Vdc as per PVSol below:
Good Day, Can you please make sure the data in PVSol Database is correct for the specified 16kW Single Phase Inverter. Something does not look correct if I compare the DC data with the Datasheet of the inverter.
Max DC Input Power should be 25.6kW
Max Input Current should be 96A
Max Short Circuit Current should be 180A
Good Day, when calculating Max Charge and Discharge Power in the Battery Setup, do you use the Max Battery Voltage (60Vdc) of the Inverter or the Max Operating Voltage (57.6Vdc) of the Battery multiplied by 220A in this example below?
When I try to change the value at 60% DOD to 10000 and do the Calculate cycles then that value just returns back to the values that it was. Nothing changes.
Also please give me the formula to determine a batteries DOD at 60% from the datasheet.
Good Day, I want to make sure if my calculations are correct. I added a Dyness PowerBlock Max 16kWh battery to the database. Please just check if my Discharge Cycles are correct below:
Good Day, How do you change the Roof Pitch or Roof Angle without deleting any configurations?
And also, why is the inclination not the same as the Roof Pitch when my system is setup for flat roof mounting?