Tolerance criteria for max input current


fpWE

Recommended Posts

  • fpWE changed the title to Tolerance criteria for max input current

Hi fpWE

1 hour ago, fpWE said:

What are the short and long term consequences for the inverters when sizing strings in each of the tolerance bands as described in PVSol?

One purpose of PV*SOL is to support you in paying attention to plant safety. Some rules should not be changed (open-circuit voltage), some changes of rules could lead to smaller parts saving money but tolerating more losses in some situations.

1 hour ago, fpWE said:

How does the range of these intervals are defined? Is it the manufacters input?

The configuration limits used for the checks are defined per project. Please have a look into our online help (reachable in many contexts using F1): https://help.valentin-software.com/pvsol/2023/en/pages/inverters/configuration-check/#configuration-check-mpp-tracker

It is a mixture of manufacturer input of the component values and the configuration check tolerance limits which you could set via the configuration limits.

Does this clarify your question?

Kind regards
Frederik

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...