Torbjørn Heimvik Posted May 16, 2023 Report Posted May 16, 2023 Hi! In the input fields for voltages (AC) for inverter types, should we enter phase voltage or line-line voltage in the field "nominal voltage"? (See below for Growatt MAX 50KTL3 XL). Quote
developer_fw Posted May 22, 2023 Report Posted May 22, 2023 Hi Torbjørn Heimvik On 5/16/2023 at 11:00 AM, Torbjørn Heimvik said: should we enter phase voltage or line-line voltage in the field "nominal voltage"? In PV*SOL we use the phase voltage. I did have a short look into besaid product and some further products of Growatt, some entry is missing the nominal voltage completely. I forwarded your request to our database team so we can contact the manufacturer to update the values in our database. Kind regards Frederik Quote
Torbjørn Heimvik Posted May 31, 2023 Author Report Posted May 31, 2023 On 5/22/2023 at 12:38 PM, developer_fw said: Hi Torbjørn Heimvik In PV*SOL we use the phase voltage. I did have a short look into besaid product and some further products of Growatt, some entry is missing the nominal voltage completely. I forwarded your request to our database team so we can contact the manufacturer to update the values in our database. Kind regards Frederik Hi! That is highly appreciated. I have seen several places that the data is not fully correct. For instance, see the screenshot from PVSOL and datasheet attached. Not all values are correct in PVSOL according to datasheet. MID 25~40KTL3-X.pdf Quote
developer_fw Posted May 31, 2023 Report Posted May 31, 2023 Hej Torbjørn Heimvik Thank you for reporting. I forwarded it to our database team, which you can also contact directly in the future if you wish: database [at] valentin-software . com Kind regards Frederik 1 Quote
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.