Dear comunity,

The M3 inverter has just 8 strings on 4MPPT,

is this a problem on PVSOL.

Can someone help me to understand if it is necessary to check in future if the number in PVSOL is equal with the number in reality?

Thank you.

Best regards.

image.png

Posted

Hi CodrinSomesan,

the number of DC inputs is not checked in the configuration section, since it is possible to combine strings before the DC input. You can use DC combiner boxes or Y connector cables or the like


image.png

 

Hope that helps, kind regards,

Martin

  • Thanks 1
Posted

Hi Martin,

unfortunately your answer is not helpful. My question was:

If I have 12 strings (technic just 12*2 connectors) How is possible to calculate 13 or more without any label that is necessary to make aditional activities. And by the way, all is proposed to be connected in series, the connector that you propose is useless if the system offer only the solution for connection in series!

Codrin

Posted

Hi Codrin,

thank you for clarifying your question. The number of strings in the configuration section is independent from the number of DC inputs of the inverter. When you connect two strings (=parallel strings) to two DC inputs on one tracker, they are combined inside the inverter. If you combine them outside of the inverter using whatever connector you want, you get the same results.

If in PV*SOL you read 3 strings x 14 modules in series, it means that you have three parallel strings of 14 modules each. If you have two DC inputs per tracker and you want to connect three strings, you'll have to use at least one connector (like the Y connector shown above) outside of the inverter.

But you are right, we could give a notice to the user that the total number of strings is exceeding the number of DC inputs. Thanks for pointing that out.

Kind regards,

Martin

  • Thanks 1
Posted

Dear Martin,

thank you for your prompt response.

I understand the logic of this type of connection, but when I put 3 strings in parallel I am pretty sure that I will have problems with the current value. I will check my configuration and I will return with example.

Even for panels ~400W, the current will be ~3*12A=36Amp quite enough over max MPPT current.

Any way, If I will met this again I will return with example. In the meantime I will be careful with configuration. 

Thank You.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...