thanks a lot for your question. The thing is that the ABB Trio 27.6 kW inverter has to MPP trackers. If you connect 20 Jinko PV modules with 315 Wp on each of them, you will have a DC side power of only 2 * 20 * 315 Wp = 12,6 kWp, whereas the inverter has a rated power of 27.6 kW. The inverter will be underdimensionened by more than 50%, which one try to avoid because of the relatively high inverter losses.

But anyways, you can configure the system as you wanted: Just choose the Jinko modules on the PV module page and enter a total number of 40 modules there.

40 Jinko 315.png

Then switch to the inverter page and enter your inverter manually. When you click on the red cross or green ticks left to the configuration table, you'll see the configuration check in order to verify what is wrong with your system:

ABB Trio 27.6kW 40 Jinko 315.png

 

You see that for the MPP voltage and current limits everything is fine, but when you look at the inverter level (marked with a red cross in the tree view), you'll see that the dimensioning factor is only 45 %, while it should be around 100 %:

ABB Trio 27.6kW 40 Jinko 315 Dimensioning factor.png

 

I hope that helps, kind regards,

Martin

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...