Down-regulation on account of the max. AC Power/cos Phi


Recommended Posts

Posted

Hi, 

We are having some discussions here regarding the  results of the "Down-regulation on account of the max. AC Power/cos Phi".

We made some scenarios (different designs) 3MW pv-plant and in one design we got a high value of losses due to down-regulation on account of the max. AC Power/Cos Phi.

Is this due to a "too high" sizing factor of the inverter? Or is there other parameters playing here?

Would be highly appriciated if you could explain and elaborate the losses incorporated in this "down-regulation on account of the max. AC Power/Cos Phi".

 

BR
Daniel

Posted

Hi Daniel,

most probably the down regulation on account of the max AC power is due to the sizing factor, yes. In general, those losses increase with an increasing sizing factor. Also be sure to simulate those losses in 1min resolution. In 1h time steps this effect can't be simulated realistically.

But if you want, you can send over a project so that we can have a look in detail.

Kind regards,

Martin

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...