Image an Installation of 1000+ PV Modules, we will have to do 1000 times the configuration process to calculate to outcome...

 

How can we do this all in once ?

Also the configuration is giving an red X. The max income is not set right in PVSOL, see image

 

Enphase datasheet.PNG

ENphase PVSOL.PNG

Posted

Hi Remu,

you can use the Enphase inverters in the automatic or manual configuration like any other inverter as well. Here in my example I have 44 modules on the roof, so I use 44 Enphase inverters:

image.png

 

You can also select all Enphase inverters using the link under "Suggest Configuration", and let PV*SOL search for a valid configuration by clicking on the arrow.

Regarding the DC and AC power values of the Enphase IQ7-60. Its values are correct in the database:

image.png

You will have to allow for sizing factors (DC power / AC power) of above 140%. You can do so by clicking on "Configuration Limits" and then set the upper limit to 150 for example:

image.png

Hope that helps, kind regards,

Martin

  • Like 1

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...