Dear,

I have a problem with system configuration limits. I want to simulate ground mounted system and while I want to configure it my max system voltage module is 1000 V but inverter that I used have max. input voltage 1500 V and if I want to put 24 module (Uoc=50,15 V) in string, there is error occured.

 

Best regards!

 

 

  • 3 weeks later...
Posted

Hi Brunomonti,

sorry for the late answer, your question got stuck in the approval queue..

The maximum voltage is the lowest value of the following three values:

  • Maximum system voltage of the modules
  • Maximum input voltage of the inverters
  • Maximum system voltage set in the options (if it was set)

 

The open circuit voltage of the modules is calculated at -10°C if not specified otherwise.

image.png

 

Hope that helps, kind regards,

Martin