Hi All,

I have created a nice system, unfortunatly the customer is not allowed to feed into the grid.
Now he has asked us to design a battery system to store the energy.

Unfortunatly or I am doing something wrong or I encounter a bug...
The problem is that with or without batteries there own usage part remains exactly the same.
What I can see in the results is that on a sunny day also the betteries are not being charged.
Can someone see if I am making a F*up ?

Greetz Johan

 

image.thumb.png.096000fcae7f483bb814f8738fdcbed7.png

 

image.thumb.png.5232b4cf03376262d9058ab943e33e2b.png

image.thumb.png.6039399a9d4547d30a8120fb585a31ce.png

image.thumb.png.890462bba0bd24425ae4371df02434b9.png

Posted

Dear Johan

thank you for the project file. In this case, the display of the connection of the DC intermediate circuit coupling of the battery system in PV*SOL is a bit misleading. In the 3D environment, there are 4 inverters, all of the same type and with the same configuration layout (2 x 15 on each MPP tracker). So, in the PV*SOL main software, these 4 inverters are displayed as one group (4x inverter xy). The DC battery system, which consists of 4 units, appears to be connected to the group of 4 inverters (one battery system on one PV inverter). But, unfortunately, our simulation core realizes that the shadows on the PV modules over the 4 inverters are not the same and calculates each inverter separately. The DC battery system, scaled by factor 4, then is only connected to the first of the 4 inverters. So, in the simulation, the battery system only sees the PV energy from inverter one, which is far less than the load profile, and this is the reason why the battery system is never charged.

We will make that clearer in the upcoming release in order to avoid PV systems with that kind of confusing (or wrong) connection.

Hope that helps, kind regards,

Martin

Posted

Hi Martin,

Ha yes, now when I set it up (software wise) with 1 big string inverter (80kW) in the 3D enviromentand the in the "battery systems" 4x 20kW hybrid inverter it does seem to work.

But it is strange that with this setup in PV*Sol you cannot create a correct simulation for a hybrid system.
Will this be adjusted in future updates?

Greetz Johan

  • 3 weeks later...
Posted
On 2/13/2023 at 11:58 AM, Johan said:

Will this be adjusted in future updates?

Yes, we will make that clearer in the upcoming release in order to avoid PV systems with that kind of confusing (or wrong) connection. In order to have that exact system that you were trying to simulate, it will take us some more measures, since there are performance algorithms involved that we don't like to destroy by accident :)

Kind regards,

Martin

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...