Bas Posted August 10, 2022 Report Posted August 10, 2022 Could it be that the parameters in the database of inverter APSystems DS3 are incorrect in PV*SOL? Under DC section: "Max. Input Current in A" is set to 20 A I believe this should be 40 A because it seems to be the total of both of the two inputs. Just like with other inverters that have two inputs. Quote
developer_fw Posted August 10, 2022 Report Posted August 10, 2022 Hi Bas, thank you for this info! Regarding the datasheet (https://www.shinetech-power.de/wp-content/uploads/2021/11/Shinetech_APSystems-DS3-L.pdf) you are correct. I forwarded it to our database team which will contact APsystems, since the manufacturers put their data into our online database themselves. Meanwhile you could copy the database entry to be able to simulate your projects. Kind regards, Frederik Quote