Hello everyone,

I am redesigning the string layout of an existing PV system after removing some modules.

The physical module layout should remain as close as possible to the existing installation. In the new design, every string must have exactly 19 modules in series.

I have two separate questions:

1. Some 19-module strings have to run across several separate roofs. The roofs have the same tilt and orientation. Is it possible in PV*SOL to define one electrical string whose modules are placed on different separate roofs?

2. Independently from that, some strings have to be connected in parallel, for example two separate strings with 19 modules each as one parallel string group. How should this be modelled correctly in PV*SOL?

The strings crossing several roofs are not necessarily the same strings that are connected in parallel.

My main question is:
Can PV*SOL handle both cases in one project, while keeping the real physical module placement as much as possible?

If this is not possible directly, what would be the recommended workaround for a realistic yield comparison?

Thank you very much for your help.


 

Screenshot 2026-07-01 142616.png

Posted

Hello,

Thank you for your inquiry.

19 hours ago, MONA said:

1. Some 19-module strings have to run across several separate roofs. The roofs have the same tilt and orientation. Is it possible in PV*SOL to define one electrical string whose modules are placed on different separate roofs?

You can configure multiple module areas on different roof areas together. First, define which modules should be configured together. Select the desired modules from the first module area, right-click on the selected modules, and choose "Add to 'Define Module Areas' Dialog." Then use the dropdown menu in the top menu bar to switch to the second building.

image.png

Now select the desired modules of the second module area, right-click on the selected modules, and choose "Add to 'Define Module Areas' dialog." Then click the "Define Module Areas for Configuration" button:

image.png

You can rename the module areas if necessary (right-click → Rename). Then click "Configure":

image.png

In the inverter configuration window, select both module areas and click "Configure module areas together":

image.png

Select both checkboxes for "Polystring configuration" and "Connect strings with the same number in series," and assign both module areas to string 1:

image.png

String 1 now runs across two separate roof areas:

image.png

20 hours ago, MONA said:

2. Independently from that, some strings have to be connected in parallel, for example two separate strings with 19 modules each as one parallel string group. How should this be modelled correctly in PV*SOL?

You have already implemented the parallel configuration of two strings, each with 19 modules, on the same roof area:

image.png

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...