Hello. can i have some guidance on how to input export limitation on a design and how to know its reading right on a report. my design has an install a generation capacity of 170kW, but the export has to be limited to 40kW. I've added the 40kw on the AC main options to set the limitation, but on the report its still showing a lot of export back to the grid.

i would assume it would only be showing the 40kw going back into the grid but in kwh? 

Export Limit on AC.png

Lyon Leisure Limited PV Report Option 1 Rev E.pdf

Posted

Hi Lorton,

Thank you for the question.

Feed-in limitation prevents a specified output power from being exceeded at a certain time when feeding into the grid. That is why it is specified in kW.

In your project, the consumption seems to be constantly so high that the output of 40 kW is very rarely exceeded at the feed-in point.

The amount of energy fed into the grid in kWh over an entire year can be higher than the maximum permitted feed-in power in kW.

For example, if 40 kW is constantly supplied to the grid for two hours after consumption has been subtracted, 80 kWh is fed into the grid. However, the limit of 40 kW feed-in power is not exceeded at any time.

Kind regards

Mikio

 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Unfortunately, your content contains terms that we do not allow. Please edit your content to remove the highlighted words below.
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...