Mikael Posted August 26 Report Share Posted August 26 Hi I have a setup with 4 inverters, and the feed-in to the main panel must be max 200A in total. The inverters are all same model and size, and each at 70A. So the total are 280A How do we set this up correct in PV sol? Thanks, Quote Link to comment Share on other sites More sharing options...
JBZ Posted September 3 Report Share Posted September 3 you have to recalculate the 200A to kW limit =138kW and check the grid limit box ( not the inverter limit box ) Quote Link to comment Share on other sites More sharing options...