April 21, 201511 yr comment_373 Hello, My name is Ahmad Elghobashy from Egypt I do have a question and don't know what to do , and I think maybe you can helpI have a string of 20 modules of Jinko solar panels JKM 310Wp now from the data sheet the open circuit voltage is 45.9 V So the total string open circuit voltage is 918 V now in the system check I get 1018 V So the max. allowed open circuit is exceded but I don't know why there is a 100 V over the stated in the data sheet Best regards, Ahmad Elghobashy Egypt Report
April 23, 201511 yr comment_376 Hello Mr. Elghobashy, the open circuit voltage specified in the data sheet is only valid for STC conditions, ie 25 ° C module temperature. The lower the module temperature, the higher the open-circuit voltage is. For your module, this value is -142.29 mV / K. In our system check, we test the system under extreme conditions, that you can define yourself. The default is to calculate the maximum voltage at 1000 W / m² and -10 ° C. If you are planning mostly in Egypt, you should here rather enter 1100 W / m² and + 5 ° C. You can change these values on page „inverters“. Klick the link Configuration limits. On page Miscellaneous you can change the values. Best regards, Rainer Hunfeld Report