  1. Just to clarify on this matter, If our DC/AC oversizing ratio is not 100%, then the clipping we need to put should not be the export limit (or capacity) we want divided by the total TIC (DC kWp). Example, We have installed 1300kWp of panels (DC), and connected it to 1000kW of inverter (AC), the grid/DNO has asked for export limit of 250kW. Solution: 250/1000 (for AC) which is 25%, and that should be the input for the clipping. if we device the 250kW by the 1300kWp, then the oversizing of the inverter has not been considered. Can someone please clarify this?
×
×