Please explain: Even though cable size is calculated for <1% losses, but cable size should also be compliant to maximum rated/ current carry capacity of cable being selected:
100kW Inverter is rated for 145Amps 3phase at STC.
pvsol calculated cable size to be 16mmsq. for 10meter length (0.76% loss) , 16mmsq has max. current carrying capacity to be 56amps. Which is NOT feasible design, should be at least 70 sqmm.
Please guide/explain design functioning for the above.
Regards,